Floating may have been a wrong term to use. I don't know how else you would call a disconneted footer that ground water could flush out. Again, I don't know your situation. I am thinking you went with historical data that said your footings are high and dry and will never have dissipating effect. |
|
Manfred Knobel Moss Pointe Builders, Inc. |
|
|
Brawler
 Basic Member
 Posts:186
 |
| 16 Dec 2008 11:18 PM |
|
I have 300' 3/4 pex poured in 5 to 6 inchs of concrete to act as a sink for any extra heat from the domestic solar hot water system during heating season like in the middle of the day when everyones at work.. Part of the slab will also have several hours of solar heating during the winter. I ordered the crete with charcoal colored pigment so i wont have to finish the floor, and it will also absorb more heat. The basement pex is strictly for solar . the other two floors will be normal radiant in 2 inch light concrete and a hot water heater. |
|
|
|
|
Brawler
 Basic Member
 Posts:186
 |
| 16 Dec 2008 11:31 PM |
|
Manfred, i used no historical data and i have no idea what a dissipating effect is. |
|
|
|
|
Manfred
 Basic Member
 Posts:200
 |
| 17 Dec 2008 12:51 AM |
|
brawler, with dissipating I was refering to the erosive potential of your footer material. |
|
Manfred Knobel Moss Pointe Builders, Inc. |
|
|
Alton
 Advanced Member
 Posts:754
 |
| 19 Dec 2008 08:28 PM |
|
In my opinion, Superior Walls are set on tamped gravel for a couple of reasons: 1. Precast Superior Walls can be set in any season without worrying about concrete freezing. 2. Tamped gravel allows the walls to be adjusted in elevation to be level. |
|
Alton C. Keown Residential Designer and Construction Technology Consultant Auburn, Alabama E-mail: alton at auburn dot edu |
|
|
TLC-ICF
 New Member
 Posts:90
 |
| 01 Jan 2009 09:20 PM |
|
Thanks for all your input. Looks as if most here are of the same opinion as I am. I believe it is an inferior not superior wall system. With a lack of strength, a lack of waterproofing, and no footer. I just hate to see not real knowledgeable home owners sucked in with a high powered sales pitch. Any other comments welcome. |
|
|
|
|
Brawler
 Basic Member
 Posts:186
 |
| 01 Jan 2009 09:57 PM |
|
TLC, Just curious if you would consider block walls better than superior walls? I would sure like to know of some real life stories that you have witnessed with Superior Walls that would validate your concerns. Your concern for "not real knowledgeable home owners" Is appreciated. |
|
|
|
|
Rob
 New Member
 Posts:16
 |
| 18 Feb 2009 02:01 PM |
|
I think what saddens me most is all the negative talk about one product over another. As a 47 year old building professional it's been an interesting journey of endless education with all types of building systems. I started laying block in my teens and worked my way to owning my own concrete company. We poured basements and lay block in NY and when the customers requested them, we installed ICF's for many of the projects in Florida. It's been my experience for over 30 years of building with concrete that they all have their disadvantages. And yes, they also have their benefits. The nice part about that is they all play a very important role in building 'green'. Concrete is a sustainable product. It's here for centuries. It would be good if we all remembered that.
It's true, one product in your particular part of the country, might have an advantage over another, unfortunately if its installation process is tainted, it to will fail miserably. It doesn't matter if it's block (CMU's), poured, ICF's or Superior Walls precast panels, the fact is; if your not willing to stand behind it, and guarantee what you say it will do, than the choice by the customer should be easy.
I'm sure my comments will be profoundly ridiculed by all the highly intelligent professionals that I've had the honor of reading about. Frankly it just makes me sad. The fact is it proves that negative talk encourages a negative outcome. Maybe we'll learn that as we sink even deeper into one of the greatest building depressions this industry has even seen. Then again, probably not.
|
|
| 'Build a Legecy, build with concrete' |
|
|
greentree
 Basic Member
 Posts:211
 |
| 18 Feb 2009 06:17 PM |
|
Posted By ICFconstruction on 12/12/2008 7:49 PM We need footings to spread and support the weight of a structure. And I subscribe by the belief to keep water outside, not underneath a building. The bed of rock will drain water, under the wall and to the underside of the basement floor.
Superior Walls are not ICFs......ICFs are superior walls. I think it should be clarified that the crushed stone base IS the footing. Whether its as good as concrete or not is certainly debatable, I'm in the concrete footing camp but stone has high compressive strength. ICF...not sure if you understand hydrostatics as it relates to foundations, correct me if I'm wrong, but dont you build with bleeders and sump pits regardless of wall system? We have inspections for them here. You manage water with stone and drain tile, not build a shield on your foundation walls and hope mr. water doesnt sneak underneath. It's not as if the stone beneath your slab will not hold water just because your walls are waterproofed. |
|
|
|
|
TLC-ICF
 New Member
 Posts:90
 |
| 18 Feb 2009 07:39 PM |
|
I was just informed by an installer in North Carolina, that superior walls in N.C. are required to be waterproofed by code. I think this is needed, but the people in other states are screwed. |
|
|
|
|
Rob
 New Member
 Posts:16
 |
| 19 Feb 2009 08:46 AM |
|
<!--[if gte mso 9]>
Normal
0
false
false
false
MicrosoftInternetExplorer4
<!--
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{mso-style-parent:"";
margin:0in;
margin-bottom:.0001pt;
mso-pagination:widow-orphan;
font-size:12.0pt;
font-family:"Times New Roman";
mso-fareast-font-family:"Times New Roman";}
a:link, span.MsoHyperlink
{color:blue;
text-decoration:underline;
text-underline:single;}
a:visited, span.MsoHyperlinkFollowed
{color:purple;
text-decoration:underline;
text-underline:single;}
@page Section1
{size:8.5in 11.0in;
margin:1.0in 1.25in 1.0in 1.25in;
mso-header-margin:.5in;
mso-footer-margin:.5in;
mso-paper-source:0;}
div.Section1
{page:Section1;}
-->
<!--[if gte mso 10]>
Respectfully, the gravel is the sub-footer. There is a
(bottom bond-beam) on the bottom of the wall that serves as a footer plate. The
gravel is the item used to transfer the load to the soil just as the conventional
footer does. As long as there is sufficient soil properties (2000psf) the load
of the house will be carried down to the soil without any concern.
I appreciate your thoughts on whether or not it’s as good as
a solid concrete wall. I had the same feelings when I first started using
precast walls. The truth is, if you don’t feel comfortable using a particular
product, you really shouldn’t be using it. Murphy’s Law teaches us that if we
don’t have a sufficient amount of information, we automatically don’t like it,
ultimately, we will find as much wrong with it as possible.
Water mitigation should be a priority with any basement /
foundation system. Superior Walls will require a sub-pump system if it’s a ‘walk-up’
(total in ground). If it’s a ‘walk out’ on the back or side of the house we
will require drain tile out to day light. Here in NC we require at least 6” to
8” of gravel with a 4” drain tile around the complete foot-print of the house.
The Dept of Insurance, deems it a necessity, that ‘ALL’
basements be coated. Superior Walls is not to be exempt even though we don’t
agree with their discussion. Again, out of respect for their authority, we try
to encourage our customers to apply the least expensive method of covering
their walls. Ultimately, if there is a problem, we are the first people they
call anyway.
Please Note: ‘Waterproofing’ is a term that Superior Walls
of America does not feel comfortable with. However, Superior Walls of North
Carolina does promote the term, and will stand behind it. To clarify, we
guarantee ‘side-wall water penetration’; yes the joints are caulked with a life
time product that Bostik Corp provides and the 5000 psi concrete mix design is
recorded by a 3rd party inspection firm and inspected by a PCI
approved agency. The wall joints and concrete strength are guaranteed under SW
of NC’s umbrella.
The guarantee is Lifetime – non-transferable. 15 years –
transferable.
The reassurance of that promise lies totally on the unbelievable
success rate of the more than 90,000 units put in the ground since 1981.
Because I’m a realist, I would like to add that Superior
Walls is not a perfect product, like all construction products on the market we
need to be constantly educating ourselves and making sure they are tested and
monitored to provide the best service for the customer. I will always appreciate
those who look at Superior Walls as an inferior product. At one time I was one
of them. For the past 8 years I’ve learned the difference between assuming and
really knowing.
If you have any further concerns or questions, please feel
free to contact me, any time. rmusso@superiorwallsnc.com
|
|
| 'Build a Legecy, build with concrete' |
|
|
Rob
 New Member
 Posts:16
 |
| 19 Feb 2009 09:57 AM |
|
<!--[if gte mso 9]>
Normal
0
false
false
false
MicrosoftInternetExplorer4
<!--
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{mso-style-parent:"";
margin:0in;
margin-bottom:.0001pt;
mso-pagination:widow-orphan;
font-size:12.0pt;
font-family:"Times New Roman";
mso-fareast-font-family:"Times New Roman";}
@page Section1
{size:8.5in 11.0in;
margin:1.0in 1.25in 1.0in 1.25in;
mso-header-margin:.5in;
mso-footer-margin:.5in;
mso-paper-source:0;}
div.Section1
{page:Section1;}
-->
<!--[if gte mso 10]>
<!--[if gte mso 9]>
Normal
0
false
false
false
MicrosoftInternetExplorer4
<!--
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{mso-style-parent:"";
margin:0in;
margin-bottom:.0001pt;
mso-pagination:widow-orphan;
font-size:12.0pt;
font-family:"Times New Roman";
mso-fareast-font-family:"Times New Roman";}
@page Section1
{size:8.5in 11.0in;
margin:1.0in 1.25in 1.0in 1.25in;
mso-header-margin:.5in;
mso-footer-margin:.5in;
mso-paper-source:0;}
div.Section1
{page:Section1;}
-->
<!--[if gte mso 10]>
Waterproofing
You
are correct, North Carolina State of Building Inspections do require
waterproofing. They receive their instructions from the State Dept of Insurance
who ultimately is the ‘God Father’ of the building & fire codes.
Superior
Walls respectfully honors their authority by telling their customers to always
check with their local code Inspection office to make sure that they are in
compliance with their local county code. Unfortunately each county municipality
and each individual code official interprets the waterproofing / dampproofing
guidelines a little differently with low and high water tables all across the
state.
In
any case, Superior Walls of North Carolina will honor their ‘Limited Lifetime
Warranty’ non-transferable, 15 years transferable, for side wall water
penetration and structural integrity of the 5,000 psi concrete mix design.
Regardless of coating materials used or not, if there is a penetration of water
or moisture, Superior Walls will be on call to help mitigate the issues at hand
and try to help rectify the problem with as minimum inconvenience as possible.
Please
note that there are over 90,000 projects since 1981 that in are in the majority
of not being coated with any special waterproof material. That is not to say
they are all perfectly installed. Like all product systems in construction,
they have their isolated problems, but the percentage rate of success with
using Superior Walls is amazingly high. Obviously, your professional opinion is
one that some share, that’s the remarkable thing about our industry; it’s built
on many different ideas all working to provide a better way of life for our
customers, our families and our futures.
At
the end of the day, you must do what you think is best.
|
|
| 'Build a Legecy, build with concrete' |
|
|
jdebree
 New Member
 Posts:50
 |
| 19 Feb 2009 04:57 PM |
|
I was looking at Superior, but will probably go ICF if I have a basement at all. I thought the Superior product looked pretty good, but not as well insulated as ICF. Pricing in SC wasn't all that much more than poured concrete. As for the gravel footing- what's under a poured footing? Gravel or dirt. So why is a concrete footer necessarily better? Couldn't you have erosion under a concrete footer as well? I don't thing anything is going to erode once backfilled- there's nowhere for the gravel to go. |
|
|
|
|
GRickard
 New Member
 Posts:45
 |
| 19 Feb 2009 06:11 PM |
|
jdebree, The purpose of the footer is to spread the weight of the wall over a 24" wide area instead of having it all on a 6" area. The larger footing makes a more stable structure.
Greg |
|
|
|
|
Rob
 New Member
 Posts:16
 |
| 20 Feb 2009 10:32 AM |
|
<!--[if gte mso 9]>
Normal
0
false
false
false
MicrosoftInternetExplorer4
<!--
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{mso-style-parent:"";
margin:0in;
margin-bottom:.0001pt;
mso-pagination:widow-orphan;
font-size:12.0pt;
font-family:"Times New Roman";
mso-fareast-font-family:"Times New Roman";}
@page Section1
{size:8.5in 11.0in;
margin:1.0in 1.25in 1.0in 1.25in;
mso-header-margin:.5in;
mso-footer-margin:.5in;
mso-paper-source:0;}
div.Section1
{page:Section1;}
-->
<!--[if gte mso 10]>
RE: R-values & gravel
From my prospective the most interesting thing about the
difference between Superior Walls and ICF’s is preference. It simply depends on
the individual using the product. Both systems work. On record, both have a very
high and long success rate of return on investment. Which frankly, isn’t that
what’s most important?
The insulation R-value for Superior Walls Xi product is 16.
But as any builder knows ultimately what’s most important is not R-value, but
in fact, inside to outside air transfer ratios. If you have a guaranteed zero
air transfer, your R-values may rate as high as 40, 50 or more.
Superior Walls are cast in a quality controlled production
facility. Not outside. The 5000 psi certified concrete is poured directly to the
Styrofoam Blue Board which is a registered trademark of Dow Chemicals and is
bonded to it as a complete unit. When the panels are erected and joined
together the seams are sealed and bonded together with another registered
trademarked product, Bostik Chem-calk 915. One bead of caulk in the middle as
the walls go together, again on the inside, and than lastly a bead on the
outside to give complete insurance that they will not leak water, or air. The
fact is their air transfer propertied are at zero. Which means once the walls
are set you could accentually paint the outside, and drywall the inside and
have an unusually high R-value concrete home, as long as the ceilings,
flooring, windows and doors are sealed properly.
Realistically, there are very few products on the market
that can accomplish such a task in such a very short period of time, making it an
extremely attractive product to most owner/builders.
Gravel;
As far as gravel is concerned, understanding soil properties
is paramount. If there’s gravel, there is minimal to zero chance of any underground
hydrostatic pressures because the gravel is the vehicle that helps relieve it.
To illuminate hydrostatic pressure ultimately makes erosion
issues a thing of the past. The railroad system has used the same methodology
since the 1700’s. Superior Walls has adopted and embraced that same method from
conception in 1981.
Gravel also has a tremendous ability to evenly distribute
the weight of a house foundation or a 400 ton locomotive and carrying it down
to the soil.
Here in North Carolina
the code requires the soil to be at least 2,000 pcf (lbs per cubic foot). If it’s
not at least 2,000 pcf than one of two things can be done, the bad soil needs
to be removed and placed with good soil and packed in 8” lifts which is usually
more expensive, or just replace the bad soil with gravel.
It’s always important to remember, that gravel doesn’t
settle, soil does.
|
|
| 'Build a Legecy, build with concrete' |
|
|
PanelCrafters
 Advanced Member
 Posts:671
 |
| 20 Feb 2009 11:01 AM |
|
Posted By Robmusso1062 on 02/20/2009 10:32 AM
But as any builder knows ultimately what’s most important is not R-value, but
in fact, inside to outside air transfer ratios. If you have a guaranteed zero
air transfer, your R-values may rate as high as 40, 50 or more. Apples & Oranges dude. You are starting to sound like the 'R-50 ICF guys'. Air infiltration has nothing to do with R-Value, and never will. It's another category on a Heat Loss calculation, and there is no way to correlate air infiltration with R-Values. I do applaud the effort though...
|
|
....jc If you're not building with OSB SIPS(or ICF's), why are you building? |
|
|
tesla-was-right
 New Member
 Posts:29
 |
| 20 Feb 2009 01:20 PM |
|
Home Energy Magazine Online March/April 1997
--------------------------------------------------------------------------------
Wall R-Values that Tell It Like It Is
-------------------------------------------------------------------------------- by Jeffrey E. Christian and Jan Kosny Jeffrey E. Christian is the manager of the DOE Building Envelope Systems and Materials Program at the Oak Ridge National Laboratory, Oak Ridge, Tennessee, and Jan Kosny is a research engineer at the University of Tennessee in Knoxville.
-------------------------------------------------------------------------------- There's a lot more to most walls than meets the eye, and the R-value of a whole wall can be considerably lower than the R-value of the insulation that fills it. At DOE's Buildings Technology Center, scientists have developed a system for measuring whole-wall R-value, and have already tested several types of wall system. -------------------------------------------------------------------------------- DOE's rotatable guarded hot box is the workhorse behind the whole-wall rating label system. Sample wall sections are placed in the box, where their thermal properties can be tested in a controlled environment. Several new wall systems are gaining popularity, due to increasing interest in energy efficiency, alternatives to dimensional wood framing, and building sustainable structures. Steel framing, insulating concrete forms, autoclave cellular concretes, structural insulated core panels, engineered wood wall framing, and a variety of hybrid wall systems are a few of the new types. But accurately comparing the thermal performance of these systems has been difficult. How Wall R-Value Is Usually Calculated Currently, most wall R-value calculation procedures are based on calculations developed for conventional wood frame construction, and they don't factor in all of the effects of additional structural members at windows, doors, and exterior wall corners. Thus they tend to overestimate the actual field thermal performance of the whole wall system. In these common procedures, the user enters a framing factor (ratio of stud area to whole opaque exterior wall area). The framing factor is usually estimated, is seldom verified against actual site construction, and is frequently underestimated (see "Is an R-19 Wall Really R-19?" HE Mar/Apr '95, p. 5). Framing factors range from 15% to 40% of the opaque exterior wall area, yet lower values are commonly used. Unfortunately, the wall's energy efficiency is usually marketed solely by the misleading clear-wall R-value (Rcw).
Clear-wall R-value accounts for the exterior wall area that contains only insulation and necessary framing materials for a clear section. This means a section with no windows, doors, corners, or connections with roofs and foundations. Even worse is the center-of-cavity R-value, an R-value estimation at the point in the wall containing the most insulation. This converts to a 0% framing factor and does not account for any of the thermal short circuits through the framing.
The consequences of poorly selected connections between envelope components are severe. These interface details can affect more than half of the overall opaque wall area (see Figure 1). For some conventional wall systems, the whole-wall R-value (Rww) is as much as 40% less than the clear-wall value. Poor interface details may also cause excessive moisture condensation and lead to stains and dust markings on the interior finish, which reveal envelope thermal shorts in an unsightly manner. This moist surface area can encourage the growth of molds and mildews, leading to poor indoor air quality.
Metal-framed walls are particularly vulnerable to thermal shorts. Unfortunately, builders often attempt to solve metal wall problems by making thicker walls and adding more insulation in the cavity between the metal studs. In fact, the thicker walls have an even higher percentage difference between clear-wall and whole-wall R-value.
Figure 1. Interface details for metal and wood framing.
Measuring Whole-Wall R-values To compare wall systems more accurately, we have developed a procedure for estimating the Rww for various system types and construction materials (see "Wall R-Value Terms"). The methodology is based on laboratory measurements and simulations of heat flow in a variety of wood, metal, and masonry systems (see "How We Evaluate Wall Performance"). The whole-wall R-value includes the thermal performance not only of the clear-wall area, with its insulation and structural elements, but also of typical envelope interface details. These details include wall/wall (corner), wall/roof, wall/floor, wall/door, and wall/window connections. Table 1. Clear-Wall and Whole-Wall R-Values for Tested Wall Systems No. System Description Clear Wall R-Value (Rcw) Whole Wall R-Value (Rww) (Rww/Rcw) x 100% 1. 12-in two-core insulating units concrete 120lb/ft3, EPS inserts 1 7/8-in thick, grout fillings 24 in o.c. 3.7 3.6 97% 2. 12-in two-core insulating units wood concrete 40lb/ft3, EPS inserts 1 7/8-in thick, grout fillings 24 in o.c. 9.4 8.6 92% 3. 12-in cut-web insulating units concrete 120lb/ft3, EPS inserts 2 1/2 in thick, grout fillings 16 in o.c. 4.7 4.1 88% 4. 12-in cut-web insulating units wood concrete 40lb/ft3, EPS inserts 2 1/2 in thick, grout fillings 16 in o.c. 10.7 9.2 86% 5. 12-in multicore insulating units polystyrene beads concrete 30lb/ft3, EPS inserts in all cores 19.2 14.7 77% 6. EPS block forms poured in place with concrete, block walls 1 7/8 in thick 15.2 15.7 103% 7. 2 x 4 wood stud wall 16 in o.c., R-11 batts, 1/2-in plywood exterior, 1/2-in gypsum board interior 10.6 9.6 91% 8. 2 x 4 wood stud wall 24 in o.c., R-11 batts, 1/2-in plywood exterior, 1/2-in gypsum board interior 10.8 9.9 91% 9. 2 x 6 wood stud wall 24 in o.c., R-19 batts, 1/2-in plywood exterior, 1/2-in gypsum board interior 16.4 13.7 84% 10. Larsen truss walls 2 x 4 wood stud wall 16 in o.c., R-11 batts + 8-in-thick Larsen trusses insulated by 8-in-thick batts, 1/2-in plywood exterior, 1/2-in gypsum board interior 40.4 38.5 95% 11. Stressed-skin panel wall, 6-in-thick foam core + 1/2-in oriented strand board (OSB) boards, 1/2-in plywood exterior, 1/2-in gypsum board interior 24.7 21.6 88% 12. 4-in metal stud wall 24 in o.c., R-11 batts, 1/2-in plywood exterior + 1-in EPS sheathing + 1/2-in wood siding, 1/2-in gypsum board interior. NAHB Energy Conservation House Details. 14.8 10.9 74% 13. 3 1/2-in metal stud wall 16 in o.c., R-11 batts, 1/2-in plywood exterior + 1/2-in wood siding, 1/2-in gypsum board interior 7.4 6.1 83% 14. 3 1/2-in metal stud wall 16 in o.c., R-11 batts, 1/2-in plywood exterior + 1/2-in EPS sheathing + 1/2-in wood siding, 1/2-in gypsum board interior. AISI Manual details 9.9 8.0 81% 15. 3 1/2-in metal stud wall 16 in o.c., R-11 batts, 1/2-in plywood exterior + 1-in EPS sheathing + 1/2-in wood siding, 1/2-in gypsum board interior. AISI Manual details 11.8 9.5 81% 16. 3 1/2-in metal stud wall 24 in o.c., R-11 batts, 1/2-in plywood exterior + 1/2-in wood siding, 1/2-in gypsum board interior. AISI Manual details 9.4 7.1 75% 17. 3 1/2-in metal stud wall 24 in o.c., R-11 batts, 1/2-in plywood exterior + 1/2-in EPS sheathing + 1/2-in wood siding, 1/2-in gypsum board interior. AISI Manual details 11.8 8.9 76% 18. 3 1/2-in metal stud wall 24 in o.c., R-11 batts, 1/2-in plywood exterior + 1-in EPS sheathing + 1/2-in wood siding, 1/2-in gypsum board interior. AISI Manual details 13.3 10.2 77%
We estimated whole-wall R-values for 18 wall systems, using a computer model. We validated the accuracy of the modeling using the results of 28 experimental tests on masonry, wood frame, and metal stud walls. The model was sufficiently accurate at reproducing the experimental data.
The whole-wall R-values estimated for the 18 wall systems are shown in Table 1 along with the clear-wall R-values. A reference building was used to establish the location and area weighing of all the interface details. The comparison of these two values gives a good overall perspective of the importance of wall interface details for conventional wood, metal, masonry, and several high-performance wall systems.
In general, construction details for the wall systems chosen come from the ASHRAE Handbook and from the respective manufacturers. In the case of the metal frame systems, the details come from the American Iron and Steel Institute and other common sources.
A wall's thermal performance is often simply described at the point of sale as the clear-wall value. The results shown in Table 1 indicate that the whole-wall value could be overstated by up to 26% for these systems. These differences can be even greater with interface details that are easier to construct but that may have more thermal shorts.
Whole-Wall versus Clear-Wall
Interesting comparisons can be made using the data in Table 1 to illustrate the importance of using a whole-wall value to select the most energy-efficient wall system. It could be argued that the difference between the clear wall and whole-wall R-value represents the energy savings potential of adopting the rating procedure proposed in this paper. Most building owners assume that they have the higher clear-wall value, rather than the more realistic whole-wall value. An insulating concrete form with metal ties is prepared for testing at the Buildings Technology Center. Its whole-wall R-value and thermal mass will be measured.
Knowing whole-wall R-value could affect consumer choices. Systems 5 and 6 in Table 1 show two different high-performance masonry units. If one used the clear-wall data to choose the unit with the highest R-value, one would pick System 5, the low-density concrete multicore insulation unit, because its clear-wall value is 19.2 compared to 15.2 for System 6, expanded polystyrene (EPS) block forms. However, if one used the whole-wall data, one would choose just the opposite, because System 6 has the higher value--15.7 compared to 14.7 for System 5. Also, the whole-wall value of the foam form system is actually higher than the clear-wall value by more than 3%. This illustrates the effect of the high thermal resistance of the interface details.
Systems 7, 8, and 9 are all conventional wood frame systems. Note that the details affect the whole-wall R-value more for 2 x 6 walls than for 2 x 4 walls. The ratio of Rww to Rcw is about 90% for the 2 x 4 walls and 84% for the 2 x 6 wall.
Comparing System 11, the 6-inch stressed-skin panel wall, to System 9, the conventional 2 x 6 wood frame wall, shows that the Rcw for the former (R-24.7) is 51% higher than that for the latter (R-16.4). However, the figures for the Rww are R-21.6 to R-13.7 respectively, an improvement of 58%. As this example shows, advanced systems will generally benefit from a performance criterion that reflects whole-wall rather than clear-wall values. How We Evaluate Wall Performance To determine whole-wall R-value, we test a clear-wall section, 8 ft x 8 ft, in a guarded hot box. We compare experimental results with sophisticated heat conduction model predictions to get a calibrated model. Next, we make simulations of the clear-wall area with insulation, structural elements, and eight interface details--corner, wall/roof, wall/foundation, window header, windowsill, doorjamb, door header, and window jamb--that make up a representative residential whole-wall elevation. Results from these detailed computer simulations are combined into a single whole-wall steady-state R-value estimation. This estimation is compared with simplified calculation procedures and results from other wall systems. The user defines a reference wall elevation to weigh the impact of each interface detail. For each wall system for which the whole-wall R-value is to be determined, all details commonly used and recommended (outside corner, wall/floor, wall/flat ceiling, wall/cathedral ceiling, doorjamb, window jamb, windowsill, and door header) must be included. The detail descriptions include drawings, with all physical dimensions, and thermal property data for all material components contained in the details.
Beyond R-Value The R-value is only the first of five elements that are needed to compare whole-wall performance. The other four elements are thermal mass, airtightness, moisture tolerance, and sustainability. We are working on standard ways to measure thermal mass, airtightness, and moisture tolerance. For some systems all five factors are important; for others, only whole-wall R-value is relevant. Thermal Mass Benefit Wall systems with significant thermal mass have the potential--depending on the climate--to reduce annual heating and cooling energy requirements below those required by standard wood frame construction with similar steady-state R-value. The thermal mass benefit is a function of climate. Effective R-values for massive walls are obtained by comparing the massive wall to light-weight wood frame walls. However this effective R-value is only a way to determine the link between the thermal mass of the wall and annual space heating and cooling loads, or a way to answer the question "what R-value would an identical house with wood frame walls need to obtain the same space heating and cooling loads as the massive walled house?" The term cannot be generally applied to a given wall type.
A procedure to account for thermal mass was used to create the generic tables found in the Model Energy Code (MEC) for all thermal mass walls with more than 6.0 Btu/ft2 of wall thermal capacitance. The tables have been in use since 1988. Customized tables can be used to show code compliance with the prescriptive Uw requirements in the MEC that are based on wood frame construction.
Airtightness Users of the DOE Buildings Technology Center follow a combination of ASTM Standards C236 or C976 (ASTM 1989) or E1424 and E283 (ASTM 1995) to measure air leakage and heat loss through clear-wall assemblies under simulated wind conditions ranging from 0 to 15 mph. Varying the differential pressures from 0 to 25-50 Pascals (Pa) simulates the extremes to which a wall is exposed in a real building. The test specimens contain one light switch and one duplex outlet connected with 14-gauge wiring that spans the width of the wall. Because heat loss in a building can be as high as 40% due to infiltration, it is important to include this performance parameter, but the quality of workmanship on the construction site, as compared to a laboratory specimen, must be considered. A second complicating factor is that materials may shrink or crack over time, and this will change the leakage. We will never completely predict the impact of workmanship on energy loss in buildings. What is important is to establish a uniform baseline for all wall systems.
Moisture Tolerance The wall's moisture behavior, like the benefit of thermal mass, is a function of climate and building operation. Annual moisture accumulation due to vapor diffusion of a particular wall system can be estimated by computer simulation. It is harder to estimate moisture accumulation due to air flow into the wall. It is important, in a long-lasting wall assembly, that the wall have the ability to dry itself out if it is built wet or picks up moisture due to a leak. The drying rate can be modeled and measured in the laboratory. The potential for moisture accumulation over specific full annual climatic cycles can also be modeled by heat and mass transfer codes such as MOIST (available from the National Institute of Standards and Technology, Special Publications 853, Release 2.1) and MATCH (available from Carston Rode, Technical University of Denmark, Department of Buildings and Energy, Building 188, DK-2800, Lyngby).
Systems 12 through 18 are all metal-framed. On average, the whole-wall value for these seven systems is 22% less than the clear-wall value. Metal can be used to build energy-efficient envelopes, but not by using techniques common to wood frame construction. The conventional metal residential systems reflected in Table 1 do not fare as well, compared to the other systems, when the whole-wall value is used as the reference. For example, if one is considering either System 6 (EPS block forms) or System 12 (a 4-inch metal stud wall), the clear-wall R-value is about the same--R-15. However, if the comparison is made using the whole-wall R-value, the EPS block form system has a 45% higher value--R-15.7 compared to R-10.9. A standard metal frame wall section before insulation and drywall is installed.
Whole-Wall versus Center-of-Cavity
We also compared whole-wall R-values to center-of-cavity R-values. When a real estate agent or contractor states the R-value of insulation across the cavity to a potential home buyer, the implied whole-wall R-value is often overstated by 27% to 58%. If one compared metal (System 13) and wood (System 7) frames using center-of-cavity R-values, one would conclude that there was no difference, since both have center-of-cavity values of about R-14. However, the whole-wall value of the 2 x 4 wood wall system is 56% better than the whole-wall value for the metal system -- R-9.6 compared to R-6.1.
These comparisons are not meant to imply that one type of construction is always better than another. They are all based on representative details. Whole-wall R-values could change if certain key interface details were changed. The purpose of making these sample comparisons is simply to show the importance of having the whole-wall value available in the marketplace, to guide designers, manufacturers, and buyers to more energy-efficient systems. An autoclave concrete wall is stuccoed in preparation for the hot box test.
Coming Soon: A Wall Rating Label? A number of innovative wall systems offer advantages that will continue to gain acceptance as the cost of dimensional lumber rises, the quality of framing lumber declines, availability fluctuates, and consumers remain concerned about the environmental impact of the nonsustainable harvesting of wood. For instance, while common dimensional lumber systems historically represent about 90% of the market, metal framing manufacturers anticipate attaining 25% of the residential wall market by the year 2000. This projection may be a bit optimistic, but it is clear that cold form steel is set to make major inroads into the residential market. Now that a growing wall database and an evaluation procedure are available, the building industry can develop a national whole-wall thermal performance rating label. This would establish in the marketplace a more realistic energy savings indicator for builders and homeowners faced with selecting a wall system for their buildings.
Labels could also help specific systems to gain the acceptance of code officials, building designers, builders, and building energy-rating programs such as Home Energy Rating Systems (HERS) and EPA Energy Star Buildings. The whole-wall R-value procedure has been proposed for adoption in the ASHRAE Standard 90.2, the Council of American Building Officials Model Energy Code, and U.S. Department of Energy's national voluntary guidelines for HERS. Many of the documents that are available to show builders how to comply with applicable codes, standards, and energy efficiency incentive programs would benefit by using the whole-wall R-value comparison procedure.
Ultimately, wall comparisons should include five elements: whole-wall R-value, thermal mass benefits, airtightness, moisture tolerance, and sustainability (see "Beyond R-Value"). Publication of this article was supported by the U.S. Department of Energy's Office of State and Community Programs, Energy Efficiency and Renewable Energy.
Wall R-Value Terms Center-of-cavity R-value: R-value estimation at the point in the wall that contains the most insulation. Clear-wall R-value (Rcw): R-value estimation for the exterior wall area that contains only insulation and necessary framing materials for a clear section, with no windows, doors, corners, or connections between other envelope elements, such as roofs and foundations.
Interface details: A set of common structural connections between the exterior wall and other envelope components--such as wall/wall (corners), wall/roof, wall/floor, window header, windowsill, doorjamb, door header, and window jamb--that make up a representative residential whole-wall elevation.
Whole-wall R-value (Rww): R-value estimation for the whole opaque wall, including the thermal performance of both the "clear wall" area and typical interface details.
Opaque wall area: The total wall area, not including windows and doors.
Continuing research is being cofunded by DOE's Office of Buildings Technology and Community Programs and by private industry to add more advanced wall systems to the database, and to address not only thermal shorts, but thermal mass benefits, airtightness, and moisture tolerance. Industry participants so far include American Polysteel, Integrated Building and Construction Solutions (IBACOS), Icynene Incorporated, Society for the Plastics Industry Spray Foam Contractors, Hebel USA L.P., Composite Technologies, Structural Insulated Panel Systems Association, LeRoy Landers Incorporated, Florida Solar Energy Center, American Society of Heating, Refrigerating and Air-Conditioning Engineers and Enermodal.
The database of advanced wall systems is available on the Internet (http://www.cad.ornl.gov/kch/demo.html). For more information, contact Jeffrey E. Christian at Oak Ridge National Laboratory, P. O. Box 2008, MS 6070 Oak Ridge, TN 37831-6070. Tel: (423) 5...; Fax:(423)574-9338; E-mail: jef@ornl.gov.
Further Reading Kosny, J., and A. O. Desjarlais. "Influence of Architectural Details on the Overall Thermal Performance of Residential Wall Systems." Journal of Thermal Insulation and Building Envelopes Vol. 18 (July 1994) pp. 53-69. Kosny, J., and J. E. Christian. "Thermal Evaluation of Several Configurations of Insulation and Structural Materials for Some Metal Stud Walls." Energy and Buildings, Summer 1995, pp. 157-163.
Christian, J. E. "Thermal Mass Credits Relating to Building Envelope Energy Standards." ASHRAE Transactions 1991, Vol. 97, pt. 2.
Kosny, Jan and Jeffrey E. Christian. "Reducing the Uncertainties Associated with Using the ASHRAE ZONE Method for R-Value Calculations of Metal Frame Walls." ASHRAE Transactions 1995, Vol. 101, pt. 2.
Christian, J.E., and J. Kosny. "Toward a National Opaque Wall Rating Label." Proceedings from Thermal Performance of the Exterior Envelopes VI conference, December 1995.
|
|
|
|
|
retired1
 New Member
 Posts:21
 |
| 20 Feb 2009 07:09 PM |
|
"Superior Walls are cast in a quality controlled production facility. Not outside."
Please be careful, RE the above.
I for one, know that there was a SW dealer on the Western Slope of Colorado in Fruita, Co. I drove across the state to see with my own eyes the operation and was amazed that it was all exterior forming and pouring after I had been assured by phone that it was done under quality conditions. Duh!
For anyone thinking of Superior Walls, please do your homework, as I did. I had a bad experience. After there reviewing my plans I was given an e-mail quote of ~ $45.000.00. I requested it in writing, ~60 days later it arrived and I almost fell over, the written quote was ~$90,000.00. I contacted the Corp. Office and was told Sorry! We are having some problems with that Dealer, thanks for calling, Bye. Needless to say, I did not continue with Superior Walls.
The truth needs to be told. That's my story and I'm sticking with it.
|
|
|
|
|
TLC-ICF
 New Member
 Posts:90
 |
| 20 Feb 2009 09:53 PM |
|
Posted By retired1 on 02/20/2009 7:09 PM "Superior Walls are cast in a quality controlled production facility. Not outside."
Please be careful, RE the above.
I for one, know that there was a SW dealer on the Western Slope of Colorado in Fruita, Co. I drove across the state to see with my own eyes the operation and was amazed that it was all exterior forming and pouring after I had been assured by phone that it was done under quality conditions. Duh!
For anyone thinking of Superior Walls, please do your homework, as I did. I had a bad experience. After there reviewing my plans I was given an e-mail quote of ~ $45.000.00. I requested it in writing, ~60 days later it arrived and I almost fell over, the written quote was ~$90,000.00. I contacted the Corp. Office and was told Sorry! We are having some problems with that Dealer, thanks for calling, Bye. Needless to say, I did not continue with Superior Walls.
The truth needs to be told. That's my story and I'm sticking with it.
90,000.00 what were you quoting, the world trade center. from an earler post-------------is 15 years a life time????????????????????????????????????????? The guarantee is Lifetime – non-transferable. 15 years –
transferable.
|
|
|
|
|
Rob
 New Member
 Posts:16
 |
| 21 Feb 2009 11:17 AM |
|
Great stuff! Thanks!
|
|
| 'Build a Legecy, build with concrete' |
|
|