Say one uses a SCW or a SCW/open loop hybrid and say it averages 25% bleed.   Ie, 75% of the water goes back into the well and 25% is dumped.   Does this eliminate 75% of the water quality problems?  It would seem that after the water has been through the system once, there should be some reduction in hardness and reusing it again should leave less hardness available to precipitate out.  Or is the amount that precipitates out so small that the hardness doesn't change and stays supersaturated?

If this were true, it would make cost effective open loop systems available to more people.

Also, has anyone seen information on open loop water quality requirements for heating only systems?  In theory, hardness precipitating out is caused primarily by heating of the water.  Cooling the well water (like a geothermal system does in Winter) increases the water's ability to keep hardness dissolved (ie, precipitation is unlikely).   So in climates where a geothermal system could be used only for heating (use an air source AC), water quality should be much less of an issue. I would guess that iron bacteria growth is also less of a problem at low temperatures.











engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1734

--
07 Feb 2010 06:48 PM
I don't think water is significantly softened by a trip thru the coax. IMO the amount of scale buildup it takes to cause a problem is dwarfed by the amount of minerals available for potential scaling in the quantities of water used in geo
Curt Kinder

Absent data, you have only an opinion. No thing done well is as simple as it seems

www.hoviscustombuilders.com
jonrUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1042

--
07 Feb 2010 07:28 PM
That could be - although the other argument would be that it takes very little to bump it from slightly supersaturated to slightly unsaturated. In other words, perhaps once it goes a hair below saturation, all deposits stop - even though the hardness may still be quite high.

jonrUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1042

--
08 Feb 2010 08:03 AM
How about this? With a typical SCW doing no bleed (5% only when demand is high), it is feasible (ie, doesn't cost much) to just soften the water (ie, remove the hardness). Ground water flow would cause some minor replacement of the water.

heatoftheearthUser is Offline
New Member
New Member
Send Private Message
Posts:96

--
08 Feb 2010 10:19 AM
Posted By jonr on 02/08/2010 8:03 AM
How about this? With a typical SCW doing no bleed (5% only when demand is high), it is feasible (ie, doesn't cost much) to just soften the water (ie, remove the hardness). Ground water flow would cause some minor replacement of the water.



That might work if there was little to no underground water movement.
gregjUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:324

--
08 Feb 2010 10:33 AM
Posted By jonr on 02/07/2010 8:06 AM

Cooling the well water (like a geothermal system does in Winter) increases the water's ability to keep hardness dissolved (ie, precipitation is unlikely). 



I would have guessed that solubility would decrease as water temp decreases. For nearly any substance heating the solvent increases solubility. Why would it be different for water hardness?
jonrUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1042

--
08 Feb 2010 04:18 PM
Don't know, but it definitely is.

"In practice, water with an LSI between -0.5 and +0.5 will not display enhanced mineral dissolving or scale forming properties. Water with an LSI below -0.5 tends to exhibit noticeably increased dissolving abilities while water with an LSI above +0.5 tends to exhibit noticeably increased scale forming properties".

"It is also worth noting that the Langelier Saturation Index is temperature sensitive. The LSI becomes more positive as the water temperature increases. This has particular implications in situations where well water is used. The temperature of the water when it first exits the well is often significantly lower than the temperature inside the building served by the well or at the laboratory where the LSI measurement is made. This increase in temperature can cause scaling, especially in cases such as hot water heaters."
gregjUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:324

--
08 Feb 2010 05:21 PM
Now you've got me googling. I found a LSI calculator online. I'm familiar with 3 of the measurements (temp, pH and hardness) but not the alkalinity measurement. Not sure how that is measured but hopefully it's not hard to find someone who can do that.

I played around with the calculator and it looks like you can overcome high hardness and get a balanced LSI by increasing alkalinity. Seems like a simple injector to increase alkalinity might solve a lot of scaling problems. I suppose on an open loop pump and dump that could get pricy but perhaps on a SCW it would take very little to balance out the LSI?


jonrUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1042

--
08 Feb 2010 07:36 PM
Agreed, treatments other than softening (even hardness sequestering)  are worth considering.  Some treatments are at the 1 quart per 10,000 gallons rate (sounds affordable but I don't have details).

The cost of closed loop systems (to avoid corrosion) keeps many people from adopting geothermal.
jonrUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1042

--
09 Feb 2010 10:42 AM
Pool and spa companies sell test kits that include alkalinity tests. pH is also easy to change.
You are not authorized to post a reply.

Active Forums 4.1
Membership Membership: Latest New User Latest: Don1975 New Today New Today: 5 New Yesterday New Yesterday: 4 User Count Overall: 18917
People Online People Online: Visitors Visitors: 1053 Members Members: 39 Total Total: 1092

GreenBuildingTalk

Welcome to GreenBuildingTalk, the largest, most active forum on green building. While you can browse the site as a guest, you need to register in order to post.

Register Member Login Forum Home

Search Directory

Professionals Products

Get Free Quotes

Tell us about your building project and get free quotes from green building professionals. It's fast & easy! Click here to get your free quote.

Site Sponsors

For Advertising Info:
Call 866-316-5300 or 312-223-1600

Professionals Serving Your Area:

Newsletter

Read the latest GBT Newsletter!

Copyright 2010 by BuildCentral, Inc.   Terms Of Use  Privacy Statement  Free Quotes  Professional Directory  Advertising Programs