Amount of water Used in an open loop system?
Last Post 08 Mar 2008 11:39 AM by hedgehog. 5 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
Naudi2uUser is Offline
New Member
New Member
Send Private Message
Posts:49

--
07 Mar 2008 02:40 PM
In a open loop system, starting with well water at ~55F.  How many gallons are needed to produce X amount of BTU's.  I am looking for approximate numbers.  I know that there is other factors, like efficiently of unit.  Say 100 gl will produce 30000 per hour,  or is it 1000 or 100000?  I have found that the well needs produce from 6 to 10 gallons per Minute.  Thank you
Carlo

geodeanUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1264

--
07 Mar 2008 07:10 PM
The formula is Delta T * GPM* 500 = BTHh.

So if you take 10° out of the well water and you have 10 GPM *500 then you have 50,000 BTUh
Dewayne Dean
Do not argue with an idiot. He will drag you down to his level and beat you with experience.

www.PalaceGeothermal.com
Why settle for 90% when you can have 400%
We heat and cool with dirt!
visit- http://welserver.com/WEL0114/- to see my system
Naudi2uUser is Offline
New Member
New Member
Send Private Message
Posts:49

--
07 Mar 2008 07:26 PM
Ok Lets say that my house by heat loss need 50,000 btu  and my well supplies 10 gpm, the heat pump removes 10F.  How much water is used per hour at a certian Oustside temp.  I know there is a lot of veriables. 
 What I am trying to wrap my head around is,  How much water output I will be dealing with.  I found on one site that output is around 6,000 gallons per day!   That is way more than I know what to do with.  Plus it sounds very high to me.  I hope this make sence to you.
Carlo

geodeanUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1264

--
07 Mar 2008 07:44 PM
So if your heat loss is 50,000 btuh and your heat pump is running non stop in the middle of the winter, then at 10 gpm * 60 minutes in an hour * 24 hours in a day .

So 10 *60 * 24 = 14,400 gallons in a day. This would only happen on a day when it was cold enough out side to keep you heat pump going non stop. This shouldn't happen very often.. If your heat pump runs 50% of the time, then you have 7,200 in a day. 25% then 3600. Any way you look at it, it is a lot of water.
Dewayne Dean
Do not argue with an idiot. He will drag you down to his level and beat you with experience.

www.PalaceGeothermal.com
Why settle for 90% when you can have 400%
We heat and cool with dirt!
visit- http://welserver.com/WEL0114/- to see my system
Naudi2uUser is Offline
New Member
New Member
Send Private Message
Posts:49

--
07 Mar 2008 08:02 PM
Wow that is alot!   If that water is dumped on one acre that would = 1/2 inch of rain per acre per day.  That I could deal with in middle of summer, but in the winter.   Thanks for the help!
Carlo

hedgehogUser is Offline
New Member
New Member
Send Private Message
Posts:51

--
08 Mar 2008 11:39 AM
for a real world example, when i lived on the farm i heated a poorly insulated 1300 sq ft bungalow with a 3.5ton, my incoming water temps were about 58, my supply well was 47 feet deep, and i required 4 to 5 gpm early in the winter, later in the winter, close to spring i would need 5 to 6 gpms to keep it from freezing up, the well's capacity was around 6 gpm so i kept close tabs on it and ran it close to the edge most of the time, as the well also supplied my domestic water. my return well was a old wooden cribbed well that was 20 feet deep or so and only 15 feet from my supply well, i suspect the supply well was getting cooled off from the return well, this would explain why i need more water later in the winter. the return wel was not capable of accepting all the water, it over flowed daily, ran into a near by creek. this is southern saskatchewan canada, winter temps are normaly -20, sometimes dipping down to -40. this system managed to keep up but probably ran 50 minutes an hour when it was -40, or -20 and windy, so it used a considerable amount of water. in the event of a freeze up, i would switch it over to AC for a minute, you could literaly see the chunks of ice going through the flow meter. do to poor water quality this system needed regular maintainance. i had a pre filter that needed weekly cleaning, once a year i had to flush the heatpump with muriatic acid (copronickel coil required). i am much happier with my closed loop, and well insulated house.
You are not authorized to post a reply.

Active Forums 4.1
Membership Membership: Latest New User Latest: hodag New Today New Today: 4 New Yesterday New Yesterday: 11 User Count Overall: 18963
People Online People Online: Visitors Visitors: 469 Members Members: 32 Total Total: 501

GreenBuildingTalk

Welcome to GreenBuildingTalk, the largest, most active forum on green building. While you can browse the site as a guest, you need to register in order to post.

Register Member Login Forum Home

Search Directory

Professionals Products

Get Free Quotes

Tell us about your building project and get free quotes from green building professionals. It's fast & easy! Click here to get your free quote.

Site Sponsors

For Advertising Info:
Call 866-316-5300 or 312-223-1600

Professionals Serving Your Area:

Newsletter

Read the latest GBT Newsletter!

Copyright 2010 by BuildCentral, Inc.   Terms Of Use  Privacy Statement  Free Quotes  Professional Directory  Advertising Programs